Master Valve Behaviour
#3
Maybe I should have put the added part of the previous post in a separate one:

After giving this more thought and running a quick test, a better solution would be:

Change to Concurrent mode which allows more than one station to rune at the same time.
Options > Station handling > Un-check Sequential

Set master to None

Program the first valve and the station that controls the pump to start at the same time. (The pump station would need to be in a separate program).

Program the second valve to start at the time the first one stops and so-on for the rest of the valves

Set the pump station's program to stop when the last valve stops.

This could also allow the pump to start a little ahead of the first valve if pressure needs to build first.


Dan
Reply


Messages In This Thread
Master Valve Behaviour - by macca - 2015 Oct 29, 12:07 PM
RE: Master Valve Behaviour - by dan - 2015 Oct 30, 06:00 PM
RE: Master Valve Behaviour - by dan - 2015 Nov 01, 08:15 PM
RE: Master Valve Behaviour - by macca - 2015 Nov 01, 10:17 PM